I'm looking to buy this 240v induction plate and run it off of my stove range socket. The problem is I can't find a plug adapter anywhere and I feel like i'm missing something. if you guys have a solution or I'm not identifying something correctly say something.
tldr; I need tp go from NEMA 14-50p to NEMA 6-20p
stove plug
back of appliance. Are you supposed to unscrew the back and put an appropriate cord on its terminals maybe?
I need OP image to plus into the above one
thanks guys, bumping with cool stuff.
>>1035718
stovetop
>>1035704
>I need tp go from NEMA 14-50p to NEMA 6-20p
Actually, you need to go from NEMA 14-50p to NEMA 6-20R
Buy a cable with a 6-20r end on it.
Cut off whatever plug is on the other end.
Attach a 14-50p to the cut off end.
You now have a NEMA 14-50p to NEMA 6-20r adapter
ALT: buy the desired plug and receptacle and one foot of 12/3 cable - connect together
>>1035736
here is the stove top, i don't follow. Are the phases and poles correct?
http://www.webstaurantstore.com/avantco-ic3500-countertop-induction-range-cooker-208-240v-3500w/177IC3500%20%20%20208*240.html
>>1035738
>Are the phases and poles correct?
Where do you live?
>>1035742
Sorry, continental US. house is built in 2000
>>1035761
>US. house is built in 2000
The middle blade and the round pin on the stove/range conector are connected together at the service/breaker box.
The middle blade is neutral and the round pin is ground/earth.
The two outside blades are L1 and L2 which are the 'hot' wires.
Connect outside blades on plug to outside blade sockets on the receptacle.
Connect round pin and/or middle blade on plug to the pin socket on the receptacle.
A multimeter check between the outside blade sockets should show ~240vac
A meter check between each outside socket and the middle blade or U-ground/earth should indicate ~120vac
The plate is sold by a company in Pennsylvania. It's intended for use in common USA wiring instances.